Should a/c coupled charge a battery in ESS mode?

Easysolar II GX not charging from a/c coupled PV. How can stop it exporting to the grid and make it go to the charger. Setup is ESS optimised with battery life using Pylontech US2000 and a current transformer on the incoming grid.


battery chargingAC PV Coupling
1600677821363.png (380.9 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Gat

I don't see your AC PV on the ccgx screen. How is it being monitored or was programmed into the system?

0 Likes 0 ·
2 Answers
gat avatar image
gat answered ·

The A/C coupled PV is connected to the AC 1 output and displays in the AC loads. The grid power is measured by a current transformer (CTR110000500 ).

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

Try limiting grid feedback or maybe prevent grid feed in for a bit until you are happy with battery SOC. See if it will charge up from the ac pv

0 Likes 0 ·
gat avatar image gat Alexandra ♦ commented ·

Turned of ac coupled feedback excess but it had no affect in passthru. It only comes out of passthrough when the batteries are fully charged. It is in ESS optimised mode and not batterysave.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ gat commented ·

It seems to be treating the pv like the grid basically then.

On ess with dc coupled pv the loads are fed from the grid in passthrough until they are charged or you have reached the desired SOC.

Does it still feedback even though you have turned off the feed in pv feature?

0 Likes 0 ·
gat avatar image gat Alexandra ♦ commented ·

Yes, the inverter is switched off until the batteries are fully charged and ac coupled feedback flows. Any dc coupled goes to the batteries. Once the batteries are charged it changes to absorption/discharge/bulk, the inverter now works normally and will use the batteries to discharge when there is a demand. Once there is no solar it switches to passthru and does not react to a scheduled charge window or any demand. It is more like what I would expect from a keep batteries charged configuration but it is set to ESS optimise.

0 Likes 0 ·
Show more comments
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Gat

the system is in passthru, please read the manual about that:

(see Q4)

https://www.victronenergy.com/live/ess:design-installation-manual#faq

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gat avatar image gat commented ·

Yes, I have looked at Q4 and none of them apply. Any other sugestions?

Q4

1. Grid meter not enabled.

2. Battery information is displayed.

3/4.CCL=50, DCL=50 SOC quite high, Ac current limit not exceeded.

5. UK grid code, No aux.

6. Grid to inverter <2m.


0 Likes 0 ·
gat avatar image gat gat commented ·

Have now tested with AUX and LOM disabled. No change. I have now reset them back to default settings.

0 Likes 0 ·
gat avatar image gat gat commented ·

If the passthru caused by one o the items in Q4 would it still be able to go into the abosrption mode and pass dc coupled pv to the grid? when my Easysolar II gets to about 98/99% soc it comes out of passthru and into absorption/discharge/bulk mode. It then allows a flow through the inverter.