https://www.victronenergy.nl/upload/software/VE-MPPT-Calc-3_7.xlsm
https://mppt.victronenergy.com/
Did you try one or both of these excellent Victron provided tools?
But only in an 48V system, and take a look at the calculations especially the max. output current (orange)
My maths works a 5 series string out at 255.25v @ 0c.
-25 x -0.138 = 3.45v ((temp below 25c) x (panel temp coefficent))
(3.45 + 47.6) x 5 = 255.25v