Hi, this is my first install of a Easysolar II GX. I am not sure if I am missing something in the configuration or if a hardware problem. I have an current transformer attached to grid tails, with no dc coupled solar(will add later.). I do have ac coupled solar on AC1 out. No real load on AC1. ESS assistant has been added and configured. I setup a scheduled charge and this also does not work. Any help would be appreciated. see configuration details below.
VEconfig
System frequency 50Hz
Shore current 20.0 A
Overruled by remote checked
Dynamic current limiter unchecked
External current sensor connected (see manual) checked
State of charge when Bulk finished 85.0 %
Battery capacity 100 Ah
Charge efficiency 0.96
TAB: Grid
Country / grid code standard UK: G98/1 March 2019, G99/1 May 2018
LOM detection AC input 1 Type B (grid code compliant)
start P(f) at 50.40 Hz
start delay for p(F) 0.08 s
Droop for p(F) 10.0 %
Use Aux1 (if available) as disable FeedIn signal checked
Reactive power regulation Use a fixed Cos Phi
Filter time for reactive power 3.3 s
Cos phi at point 1 1.00
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 230 V
Inverter DC shut-down voltage 44.00 V
Inverter DC restart voltage 48.00 V
Low DC alarm level 48.00 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Use equalization (tubular plate traction battery curve) unchecked
Charge curve Fixed
Absorption voltage 52.00 V
Float voltage 51.00 V
Charge current 35 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 1 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
ESS (Energy Storage System) (size:1709)
*) System uses LiFePo4 with other type BMS
(This can be either a BMS connected via CAN bus or a BMS system in which the
batteries are protected from high/low cell voltages by external equipment.)
*) The battery capacity of the system is 100 Ah.
*) Sustain voltage 48.00 V.
*) Cut off voltage for a discharge current of:
0.005 C= 46.00 V
0.25 C= 46.00 V
0.7 C= 46.00 V
2 C= 46.00 V
*) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).
*) The solar converter will start reducing its output power at 50.20 Hz.
Output power will be reduced to minimum when the frequency is 52.70 Hz.
The converter will disconnect when the frequency is higher than 53.00 Hz.
*) Total installed PV inverter power is 1500 Watts.
Total installed PV panel power is 1500 Watts.
*) Relevant VEConfigure settings:
- Battery capacity 100 Ah.
- PowerAssist unchecked
- Lithium batteries checked
- Dynamic current limiter unchecked
- Storage mode unchecked
Total size of all assistants including the required
(hidden) system assistants is: 1782