First Install- stuck on passthru. Unable to charge or discharge.

Hi, this is my first install of a Easysolar II GX. I am not sure if I am missing something in the configuration or if a hardware problem. I have an current transformer attached to grid tails, with no dc coupled solar(will add later.). I do have ac coupled solar on AC1 out. No real load on AC1. ESS assistant has been added and configured. I setup a scheduled charge and this also does not work. Any help would be appreciated. see configuration details below.

VEconfig

System frequency 50Hz

Shore current 20.0 A

Overruled by remote checked

Dynamic current limiter unchecked

External current sensor connected (see manual) checked

State of charge when Bulk finished 85.0 %

Battery capacity 100 Ah

Charge efficiency 0.96

TAB: Grid

Country / grid code standard UK: G98/1 March 2019, G99/1 May 2018

LOM detection AC input 1 Type B (grid code compliant)

start P(f) at 50.40 Hz

start delay for p(F) 0.08 s

Droop for p(F) 10.0 %

Use Aux1 (if available) as disable FeedIn signal checked

Reactive power regulation Use a fixed Cos Phi

Filter time for reactive power 3.3 s

Cos phi at point 1 1.00

TAB: Inverter

PowerAssist unchecked

Inverter output voltage 230 V

Inverter DC shut-down voltage 44.00 V

Inverter DC restart voltage 48.00 V

Low DC alarm level 48.00 V

Do not restart after short-circuit (VDE 2510-2 safety) unchecked

enable AES unchecked

TAB: Charger

Enable charger checked

Weak AC input unchecked

Stop after excessive bulk unchecked

Lithium batteries checked

Use equalization (tubular plate traction battery curve) unchecked

Charge curve Fixed

Absorption voltage 52.00 V

Float voltage 51.00 V

Charge current 35 A

Repeated absorption time 1.00 Hr

Repeated absorption interval 7.00 Days

Absorption time 1 Hr

TAB: Virtual switch

TAB: Usage

Virtual switch usage Do not use VS

TAB: Assistants

TAB: Assistant Configuration

ESS (Energy Storage System) (size:1709)

*) System uses LiFePo4 with other type BMS

(This can be either a BMS connected via CAN bus or a BMS system in which the

batteries are protected from high/low cell voltages by external equipment.)

*) The battery capacity of the system is 100 Ah.

*) Sustain voltage 48.00 V.

*) Cut off voltage for a discharge current of:

0.005 C= 46.00 V

0.25 C= 46.00 V

0.7 C= 46.00 V

2 C= 46.00 V

*) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).

*) The solar converter will start reducing its output power at 50.20 Hz.

Output power will be reduced to minimum when the frequency is 52.70 Hz.

The converter will disconnect when the frequency is higher than 53.00 Hz.

*) Total installed PV inverter power is 1500 Watts.

Total installed PV panel power is 1500 Watts.

*) Relevant VEConfigure settings:

- Battery capacity 100 Ah.

- PowerAssist unchecked

- Lithium batteries checked

- Dynamic current limiter unchecked

- Storage mode unchecked



Total size of all assistants including the required

(hidden) system assistants is: 1782


MultiPlus Quattro Inverter Chargerbattery chargingEasySolar All-in-One
capture.jpg (74.5 KiB)
ess-console.jpg (63.8 KiB)
ess-console-2.jpg (58.0 KiB)
ve-config.txt (2.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
paulcupine avatar image
paulcupine answered ·

Just added panels to an existing EasySolar system and it is showing the same behaviour as you describe. Did you get to the bottom of the problem?