I bought the Victron Multiplus 12/3000/120-50 120V VE.Bus to install in my RV. My current system:
1.3 Kw solar on roof
Midnite Classic 150 charge controller
4 225 Ah flooded batteries (plan to upgrade to Lithium soon)
12.5 kW diesel generator
(1) 50 amp shore power, plus )2) 30 amp shore power connections.
Generator and all shore power go to the AC panel through a selector switch, so i can select 30, 50 or gen power and the L1, L2. N and ground wire come into the panel from that switch.
To install the inverter, I am reading and understanding the only way with this unit is to run one line L1 tp the AC panel and the other L2 through the inverter and then back to the L2 side of the AC panel, which is already separated into the 2 legs.
I understand I must separate the neutrals between L1 and L2 -separate neutral bus bars for L1 and L2).
I only need inverter AC power for one side of the panel to run my fridge and a couple of other low power outlets. I would like the solar to provide all the DC required to run the inverter during the day (with excess going to battery charging.
I've been reading this board for hours and I can't decide if it's better to return the Multiplus and buy a quattro - is that a better choice (because it has two AC inputs) for my situation - or should I continue with the plan of separating L1 and L2?
If I separate L1 and L2 as described, when I use my generator to power all three air conditioners, the microwave and convection oven, with all of the required watts pass though the inverter? Or will the inverter limit how much can go through its leg?
Thanks,
Jim Phoenix