Good morning,
The limitation of not being able to use Venus OS (Cerbo GX) to control the state of the MultiPlus (on/off/charge) or the input current limit) when there is no DMC and a VE.Bus BMS is being used is becoming a real issue for me.
I was wondering if I moved from using the VE.Bus BMS Assistant to the Two-signal BMS, if the ability for Venus OS to control these parameters is possible. I would connect Charge Disconnect from the VE.Bus BMS to Aux Input 1 and set the assistant so when open the battery is full and force to float. Then connect Load Disconnect to Aux Input 2 for battery is empty.
Would this work?