Ignore AC Input 1 in an assistant

I am looking for some information on the “Ignore AC input 1”.

When used within an assistant does it switch the relay highlighted in the schematic attached.

Thanks

Assistants
image.png (350.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

There is nothing attached.

I think the relay that you mean is the transfer relay and that will open if the programmed parameters are reached. So there is no charging from or passthrough from the grid.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bathnm avatar image bathnm commented ·

Yes that was the relay. So if Ignore AC input 1 is used to control the relay all AC into the box is switched off?

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ bathnm commented ·

Yes, no power from the AC IN will be uses.