Smartsolar 150/100 solar watts low

Hi all,

I have read some other posts from people when searching for more information, however they seem to be a bit different to what I am seeing.

I have just installed a Smartsolar 150/100 with 2.5kw of panels connected and a 24V wet cell battery bank.

I have also installed a BMV-712 between batteries and charger so that I can get some rough indication of SOC.

In a totally sunny day where everything should be working fine, the watts coming from the panels is a lot lower than I was used to seeing on the old charge controller, sometimes only around 350w is showing on the solar input section.

The charger is charging the batteries and I can see that it's doing this, and it's sitting in BULK mode.

Other posts I have read have cited the same problem with low wattage from the solar, but when the people check their charger it is actually in FLOAT mode, my charger isn't getting to this mode but seems to be reducing the input from the solar like it seems to do in FLOAT mode.

In checking the history it has actually reached absorption and float mode on a few occasions, but not many, it really should be hitting it every day with the panel capacity, sunlight and battery capacity. Typically I am using about 65 a/h of power a night, this should be replenished pretty quickly realistically with this setup.

I have triple checked settings, connections, everything seems correct.

When I run a load like the microwave or something from the inverter the watts coming from the panels jumps up to more like it should be, so it's like the charger is limiting the charge to the batteries and therefore limiting the wattage it is accepting from the panels.

I have played around with the charge current, it should be around 45A for my battery setup, I have increased it and decreased it but I have never seen the charge current get to more than about 16A according to the controller.

Any thoughts as to what might be going on ?

Thanks for your help.

smart solar charging behaviour
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

How do you have your array wired up?

What is the array's voltage reading at the Mppt?

0 Likes 0 ·
Show more comments
Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

Some screenshots of VictronConnect could help.

0 Likes 0 ·
2 Answers
Paul B avatar image
Paul B answered ·

When the Battery voltage reaches 29volts then the MPPT unit will reduce the amps/watts and this is the correct operation, even if you are in bulk mode, this is because the battery is FULL and the battery does not need them amps anymore. once it changes to float the voltage will then slowly reduce to the float level and during that period there will be zero amps, once float voltage is reach then the amps will again increase to what the battery needs plus any conected loads. (this will depend on the panels output as well)

when you turn on a load the voltage drops and thus the MPPT supplies more power from the panels for that time period


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pjulian avatar image
pjulian answered ·

Thanks Paul, I thought this was what was happening.

Why though would it still show bulk mode though if it was really in float or should be in float ?

How long would you expect that it would sit like this before it actually tells you it's changed modes ?

That seems like a strange behaviour and is confusing as well.