I have a 150/60 MPPT with a string of 12 panels (Voc = 37.4 each). It's been in place for about 3 years, but about 4 or 5 times a year I get a VRM warning that the voltage is greater than 150V, which then clears after 30 seconds or so. I've never worried about this, assuming it was just a transient issue. However I've just read @Guy comments on other posts that even if it a couple of volts over 150 then I must immediately switch off the device, and reconfigure the strings. I don't know how they are currently configured, but am I right that if the voltage is maxxing out at just over 150V , then they will be in 3 parallel sets of 4 series panels. So must I change this to 4 parallel sets of 3 panels, which will bring the max voltage to 114V which is well below the 150 limit? What is the downside to doing this?