question

swordoski avatar image
swordoski asked

How do I install the Smartshunt with parallel batteries?

What is the correct way to install the smartshunt on my battery bank ?!

I have 2 battery (12v) in parallell, and 2 VE Blue Smart 75/15 charges (synchronize charging)

Br

Marcus

SmartShuntinstallation
monitor-battery.jpg (76.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The shunt has to be connected in the negative wire that goes to your loads/chargers.


bmv-parallel.png (67.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Pieter Boomsma avatar image
Pieter Boomsma answered ·

Hi Marcus,

It depends a bit on what you want. You can see your 2 parallel batteries as 1 battery. They cannot be monitored seperate from each other so don't stare blind on that. If you don't charge the batteries from an alternator you can use the diagram on page 9 of the manual. Make sure to set Setting 69 (Auxilary input) to Starter battery or Temperature even if you do not use it (it will give you an error regarding midpoint voltage error if you don't).


8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

swordoski avatar image swordoski commented ·

Hmm...Alright @Pieter Boomsma

So i put both MPPT's on the SYSTEM MINUS side on the Smartshunt ?!


0 Likes 0 ·
Show more comments
Pieter Boomsma avatar image
Pieter Boomsma answered ·

please connect it like the picture from Matthias, That are the only right options. You have no midpoint in a parallel batterybank so you can set it to second battery.


You seem to be right on the order of disconnections, do connection visa versa.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

swordoski avatar image
swordoski answered ·

What I thinking about is, if i connect both battery negative to the shunt ?!
Option 1 or 2 or is it totally wrong ?!


option1.jpg (121.4 KiB)
option2.jpg (114.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ori-haberman avatar image
ori-haberman answered ·

I know this is an old post but I have a followup question:

I have 2 48v server rack batteries (eg4) which I want to wire in parallel to a smartshunt. In the eg4 manual it says not to jumper the batteries in parallel, rather use a properly rated busbar to connect them in parallel to avoid large currents and overheating in the end wires.

So my question is this:

In my case because its only 2 batteries, can I just connect 2 negative wires to the battery end of the smartShunt? Its not 4 batteries which would warrant a whole busbar, really just 2 5awg wires connected directly to the shunt, using the shunt as a "post"...

I know it can kindof be considered "abuse" but is it really necessary for me to add a busbar?
And then while I'm at it, I have the same question for the positive side... Can I just attach the 2 positive wires directly to a t class fuse holder?


In the continuation of the system I wil have of course a lynx distributor, I'm just wondering if I can avoid adding 2 additional busbars to my system...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.