Autostart misbehaving, Cerbo GX starting generator early

Cerbo GX with BMV712. Several times in the last week the cerbo has activated the gen start relay before the battery SOC gets down to the set point. I have SOC start enabled to go at 40% and stop at 95%. There are no other conditions set for autostart. Occasionally the system will close the relay at somewhere around 85% and run to 95%. In the menu under gen start, the readout states "running from SOC" I do not have "quiet hours" set to on. The SOC on the BMV readout agrees with the Cerbo readout. I cannot understand why it comes on before getting to 40%. Any ideas? Cerbo set to auto update, firmware is 2.58.

cerbo gxGenerator
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Is the system connected to VRM?

There is a slightly hidden feature in the advanced XLS/CSV export download that shows the reason for the generator start.

Could you check that?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ur12vman avatar image
ur12vman answered ·

Some additional sleuth work with help from Guy Stewart allowed me to find this bit of evidence.

There is a download from cloud link at the top right corner of the advanced page on VRM. Setting your date/time parameters allows a very comprehensive data dump for that time period. Try a one day download and see the huge number of data points you get.

At 1707:00 on 8-18 the system went from 87.5% SOC to 1.2% for about a second and then to 87.1%. this one second blip was enough to close the relay and start the genset which ran for 16 minutes until it reached 95% at which point it stopped.

Now to figure out why the SOC went to 1.2% for one second.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alex-solar avatar image
alex-solar answered ·

We got same problem in a system where we have:

1. Victron Quattro 48/15000/200 - 6 pcs.

2. Victron SmartSolar MPPT VE.Can 250/100 - 8 pcs.

3. Victron Cerbo GX + GX Touch 50

4. BMZ ESS 9.0 - 9 pcs.

5. Fronius Symo 10.0-3-M - 1 pc.

But after downloading the log file we saw that with SOC everything was ok.screenshot-1.png

Everytime when system goes to inverting the generator starts immediately. What could be the problem?


screenshot-1.png (66.1 KiB)