I have a Multiplus 24/5000 running on Victron lithium batteries with a VE.Bus BMS and Cerbo GX. I have wired in a 3 position switch for remotely controlling the unit, seeing as the Cerbo can't do it if you have a VE.Bus BMS.
It seems that the 3 position switch option doesn't work either. With the switch on the Multi set to ON, the unit will invert with the remote switch in either the ON or OFF position, however it will respond to the "CHARGE" position. I've checked my wiring and it's correct. You get the same behaviour with the terminal block removed completely.
Is this the same limitation of only one device being able to switch the Multi, with the BMS overruling everything else?
Would a Digital Multi Control also not work?
This seems like a pretty major oversight in the design.