khaem asked

Simultaneous MPPT and Fronius doesn't use all the PV to charge the batteries

Hello,


Here is the configuration of Quattro 48/8000:

Fronius Inverter (7kW) on OUT1

MPPT (4kW) through DC-BOX on Pylontech Lithium batt


it runs under ESS Optimized (without BatteryLife).


I don't understand why the Fronius energy doesn't go to charge the battery ... here the problem :


1570W into the grid instead of charging battery...


how can we correct this behaviour ?


I can give you more details if necessary.


Best regards,

Emmanuel

MPPT ControllersESSFroniusmppt charging
1596457245483.png (34.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @khaem,

Please update the version of VE.Configure used to program the unit. This should also update the assistants.

Then update the assistants used in this system. There was an improvement made, and this might resolve the issue.

Note that this can be done remotely using Remote VE.Configure.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

khaem avatar image khaem commented ·

Thank you @Guy Stewart (Victron Community Manager) for your answer.

I will try it today and confirm you the reaction of system tomorrow.

Best regards,

Emmanuel


0 Likes 0 ·
Show more comments
khaem avatar image khaem commented ·

Hello ;)


I have tried your solution: I upgraded the ESS assistant and everything goes well.

Thank you a lot !


For the matching curve : it's perfectly normal.

I have connected all the charge of the house to a LifeDomus domotic system the manage every little charge.

During the day, it give priority at loads and turn them off or on following the fronium and mppt power level.

I just see that it works well ;) I don't think there is an error...


Thank you again.


Best regards.

Emmanuel

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

I just had a look at the VRM data for the site;

Something else caught my attention:

It is quite unusual for the AC consumption to so perfectly match the PV inverter yield. Is there any possibility that the Fronius is wired into the AC input, and configured as connected to the AC output on the GX device?

A quick way to check is to adjust the location of the PV inverter in the GX device menu from output to input, and see what happens then.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

khaem avatar image khaem commented ·

good management of loads ? ;)

0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

How many Pylontech battery modules do you have?
Maybe the charging current is limited by the battery?!

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

khaem avatar image khaem commented ·

10 Pylontech Lithium batt so 22kWh power

charge/load limitation are at 250A ... it's ok ;)

problem is solved by upgrading ESS version.


0 Likes 0 ·