Too early cutoff when load is low

During years we optimized pwr consumption of our home, idle mode at night is around 250W-350W ish. Last night was the first our new Multigrid / LG RESU 6.5 combo was running the home by battery. Nice feeling btw.
However although minimum SOC is set to 20% system switched back from inverter to grid at 49% SOC.
My first guess - this is related to the cutoff voltage which is relatively high for small loads. If so how can I change this behavior?

ESSmultigrid
1547884900194.png (51.1 KiB)
1547885084664.png (36.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi, Lower the low voltage cutoff values.

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

vicky avatar image vicky commented ·

Txs for confirming, to better understand sensitivity of parameters I'll try now

0.005 C= 50.80 V

0.25 C= 49.90 V

0.7 C= 49.20 V

2 C= 48.00 V

0 Likes 0 ·