More Alarms debug data needed to help diagnose ESS overload

I am getting constant L1 overload alarms despite usage not being an issue. I have read the many docs and faqs that provide advice, however an alarm provides zero debug on where to investigate.

For example, an L1 overload alarm can be triggered by many things, more so with ESS, but when it happens you get no data from the subsystem that triggered the event.

This is a problem.

Multiplus-IIESSMPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Nick, yes it could/should be improved.


for your issue, I assume you found that you need to try with LOM disabled on the grid connected AC input on the Grid tab?


if there are no loads & your system is ESS, then thats what you have to do.


and if you can improve the wiring, do that. And if not, install external anti islanding device.


more details in the document you’ll have seen.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·

We have an iron running against a low base load. Every time the element kicks in (up to 2500w) it triggers an alarm. The power is first pulled from battery (up to 2100w) which makes no sense with a 1000w inverter limit and that we are on grid.

Why is it doing this?

Batteries are being drained despite being on grid and the alarms don’t give any data why.

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ nickdb ♦♦ commented ·

This is a new install with new wiring, the gauge is higher than required.

0 Likes 0 ·
Show more comments
nickdb avatar image nickdb ♦♦ nickdb ♦♦ commented ·

This only started when ESS was enabled.

The alarms clear the moment they are created.
something is off.

0 Likes 0 ·
Show more comments
anacrhy2007 avatar image
anacrhy2007 answered ·

Did you get this issue resolved?

I have exactly the same issue with not very much help from our distributor. Also only happens in ESS.
Yes, I have discable LOM, Have changed grid codes, limited inverter power,


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·

Not really no. I came to terms that it was grid related and while annoying is harmless. I still see them occasionally and they have persisted through system and battery upgrades, so nothing wrong with the kit.

0 Likes 0 ·