Apologies if I'm reheating an old topic,
I have a technical question regarding the float voltage for SmartSolar 150/35.
I have an off grid system in UK running 6 SmartSolar 150/35 MPPT’s in synchronisation, the remainder of my system consists of Venus GX, 3 Multiplus Compact 24/2000 running in parallel, a BMV702 and 683Ah Rolls 5000 series batteries all fed by 8KW of Solar PV panels.
All the kit is running on the latest firmware (the MPPT’s are running v1.50)
The 6 MPPT’s and the BMV702 are connected to the Venus GX with a mixture of VEDirect and USB and all seem to be playing nicely together and sending data to VRM.
The MPPT’s are synchronised using Bluetooth and again play nicely except for the Float set point voltage; the Rolls batteries require a float voltage of 27v, so that is what I set the MPPT’s to using the Victron Connect app (which incidentally doesn’t work on my Android phone running Lollipop), but each day the system seems to choose a different voltage set point anywhere between 26.6 and 27 volts. When the system goes into float it is very stable at whatever voltage it has chosen for the day but it is never the 27 volts I have set (I have repeatedly checked that all 6 MPPT’s are set to the same Bulk, Absorption and Float voltages).
Do you have any ideas what could be causing the problem?
Would it help if I installed a Smart dongle on the BMV702 and synchronised it with the MPPT’s to relay its voltage data directly via Bluetooth?