I recently changed my charge controller, it had developed fault and was replaced under warranty. So everything was the same. Installed charge controller, but monitor is not showing any input from the panels?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I recently changed my charge controller, it had developed fault and was replaced under warranty. So everything was the same. Installed charge controller, but monitor is not showing any input from the panels?
sorted, it's been off for a while waiting new cc, forgot to connect the neg to the loads side of the shunt. Thanks so much, had me worried the array had blown!
No I connected the neg of the cc directly to the battery! I thnk I should have put the neg on the battery side of the shunt? It's been off for a while, so might have made a mistake?
24 People are following this question.