question

nickdb avatar image
nickdb asked

enhancement request: DVCC

I have noticed that DVCC responds immediately to changes, particularly temperature changes.

Where equipment is in a warmer environment and then gets exposed to cooler air this results in rapid temperature drops and larger, sudden increases in charge voltage. This sets off midpoint voltage alarms on shunts and these transients aren't great for battery life.

Could DVCC logic not be improved, to normalise these changes (temp/voltage) over a few minutes, say 5 to 10 minutes so that changes are smoother and more gradual, eliminating transients?

Multiplus-IIBMV Battery MonitorVenus OSDVCCmppt charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Nick, the (only) temperature involved with charging is battery temperature - how can that go up and down so quickly? The mass of the battery will make for such changes to be slow always.


are you sure the sensor is properly thermally connected to the battery and/or that the right sensor is chosen in the system?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·

Looking at it in more detail the temp changes are more gradual but contribute to the broader issue. I will attach a chart. Whether it is the mppt/ESS contributing, I do see transients which ultimately set off midpoint voltage alarms.

Sensors are all correct and genuine victron parts. I have adjusted the VRM collection interval to be more granular.

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ nickdb ♦♦ commented ·

Hi, looks to me like your batteries are out of balance. 1.4V difference is a lot - no?

0 Likes 0 ·
Show more comments