question

chris18 avatar image
chris18 asked

Is it allowed to install my battery control shunt between Lithium Smart battery and BMS?

My Battery control monitor does not recognize some incoming charging from the solar and b2b booster and therefore shows incorrect capacity. To fix this the installation of the shunt between battery and BMS was recommended - is it possible?

Lithium Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Yes, you should do this.
To count all energy into and out of the battery, the "battery -" terminal of the shunt should be the one and only thing connected to the battery negative post.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

The problem with this is that the BMV can kill your battery because it can't be disconnected from the battery by the BMS.
So it will draw energy from the battery even if the BMS already disconnected all loads.

0 Likes 0 ·
Show more comments