Hi
Running AC coupled system:
Victron Quattro 10kVA firmware ver: 2653 474
Fronius Primo 4.6kWp firmware ver: 3.13.3-2
BlueNova RacPower 5.2kWh x 2 ver: 1.8
CCGX v.2.57
1. Exporting of Fronius to grid still happening even with zero feed-in etc activated. Happens when the battery is full and the load reduces quickly. This then trips the Conlog meter at the municipality end. This creates a lot of switching between grid and invert. Can this be solved?
2. Running ESS, as soon as the system reaches its 'Minimum SOC (unless grid fails)' and ESS #1 activates it reduces the production of the Fronius and does not charge the battery even when battery is only at 40% and loads of PV available. Is it possible to disable #1 completely? The battery monitor is set to BlueNova.
Regards
Jan