The Pylontech US2000s recommended charge current is 25A. I am using 4 on this system. Do I make the charge current 100A (4 x 25A) in VEConfig ?
The max of MPII & Quoattro 48 is 70A? so then should it be set to 70A?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
The Pylontech US2000s recommended charge current is 25A. I am using 4 on this system. Do I make the charge current 100A (4 x 25A) in VEConfig ?
The max of MPII & Quoattro 48 is 70A? so then should it be set to 70A?
Yes you can multiply the charge current by the number of batteries. You can check this out in the following article
https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom
Section 4.