Do I multiply charge current with the number of batteries for Pylontech?

The Pylontech US2000s recommended charge current is 25A. I am using 4 on this system. Do I make the charge current 100A (4 x 25A) in VEConfig ?


The max of MPII & Quoattro 48 is 70A? so then should it be set to 70A?

Multiplus-IIPylontech
downloads.png (615.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·
@jond
Hi

Yes you can multiply the charge current by the number of batteries. You can check this out in the following article

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom
Section 4.