Multiplus overload while on standby with shore present

Multiplus ii is setup in ups mode with 5kw generator on AC1. With generator running, the inverter shuts down when a 15a motor starts. This happens with and without power assist. This motor easily starts and runs and does not overload the generator when connected directly to the generator. Why is the multiplus even trying to take the load? Why is it overloading the inverter if the load is well under the generator's capacity (inverter should not even be interfering)?

MultiPlus Quattro Inverter Charger
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Tojohn

The load is still passing through the inverter electrically. A 15a run amperage means a higher start amperage so there would be an overload.

For loads like that a bypass switch would be beneficial.

0 Likes 0 ·
tojohn avatar image tojohn Alexandra ♦ commented ·

So the power assist feature only works up to the capacity of the inverter and not the sum of the inverter and grid/generator?

0 Likes 0 ·