Alexander Ushakov asked

SONNENSCHEIN A602 SOLAR 8 OPZV 1130 battery capacity

I installed SONNENSCHEIN A602 SOLAR 8 OPZV 1130 with QUATTRO 48/15000/200-100/100.

https://www.off-grid-europe.com/batteries/gel-lead-acid/sonnenschein/sonnenschein-a602-solar-8-opzv-1130?

According to its manual, battery capacity C10 = 908Ah and C100 = 1096Ah. Accoring to label on the battery, its C120 capacity is 1131Ah.

What number is supposed to be input to VE configure program? C10, 20, 100 or 120?

battery chargingVEConfigure 3battery capacity
image001.jpg (67.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

That depends on your average discharge rate.

If you mostly discharge with C10 you should enter that.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rainerb avatar image
rainerb answered ·

Hi Alexander,

I have also a bigger A602 Sonnenschein 24V battery bank in operation for over a year. For such a big battery bank as yours, I would strongly recommend to use an external battery monitor (eg. BMV712) and not using the internal battery monitor of the Multiplus.


First I tried also only the Multiplus battery monitor but the SoC always drifted completely away especially when the bank was not always fully charged for a few days (autumn, winter). Especially when drawing much power the divergences are getting higher and higher (because there is no peukert correction in the Multi). The VEConfigure battery monitor settings are just rough guesses and therefor (at least for me) not a reliable synchronisation point.

Though, my previous very small battery bank with Sonnenschein SB330 worked quite OK with the Multi battery monitor.


With the BMV712 you can define exact settings for the 100% sync point and the calculations are far more accurate for different discharge currents (see peukert exponent) and of course there is the current measurement via the shunt. I would suggest to invest ~200Euro for the BMV and in the future you will be far more satisfied with your system.

My charger settings are: 29,2V Absorption for max 2h per day and 28,2V Float voltage.


Regards

Rainer


15 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexander Ushakov avatar image Alexander Ushakov commented ·

Rainer,

that's definitely an option to try, Thank's for this advice, I hear it for the 2nd time already about BMV and I'm about to place an order.

1. What's your charge efficiency coefficient in VEConfigure? You do not of course enable built in battery monitor and configure BMV directly. So, you must have input it somehow into BMV - I'm not familiar yet how it's done in your case.

2. Do you have a sharp rise in SOC right after 2 hours of absorption are over each day?

3. What charge current do you have within these 2 hours of absorption? Mine is rather low for these large power bank, since I want to get it directly from solar panels - 0-50A in the morning. It's just around 5A per 100Ah of C10, which is definitely too low to carry-out correct charging as prescribed in the battery manual (20A per 100Ah of C10 is optimal as it's written). I guess if I had 100-200A charge current from solar panels then 2 hours of absorption at 2.45V would really be enough to fully charge it from 85% to 100%. And in this case correct charging procedure would be completely and precisely fulfilled. Since I cannot reach 100-200A of charge current yet, I decided to lower absorption current from 2.45V to 2.4V, what allowed me to overcome limitation of 2 hours per day for absorption duration, so that not I can charge with 2.4V for the whole day once a week, what also meets the requirements of the manual, and the switch to flat at 2.3V.


Now, when I decreased charge efficiency coefficient from 95 to 85%, batteries started being charged longer as expected. So, they are not full so far by now (noon), since all same sunny days before they were at 100% by this hour. My understanding is that 85% is closer to correct number of charge efficiency than 95%. I’ll keep observing.

0 Likes 0 ·
Show more comments
Alexander Ushakov avatar image Alexander Ushakov commented ·

Rainer,

I instaled BMV712 with 500A shunt.

What looks suspicious is that I do not know now where 240W of enrgy go to:

Before my quattro consumed 30W, now according to these readings it should consume 240W, but it's not true, because it does not get that warm and fan speed is pretty low.

So I think there's something wrong with setup.

1. Is it the same with your readings?

2. What Peukert exponenta did you input?

3. Did you replace your shung with 1000A one?

0 Likes 0 ·
1600074962102.png (27.3 KiB)
Show more comments
Alexander Ushakov avatar image
Alexander Ushakov answered ·

What makes me nervous is that at around 12:30 every day battery state of charge is quickly increased from 92 upto 100%. It's not good. I guess it's due to some data, input incorrectly into VE Configure. Can you suppose what it might be?


1594738578616.png (584.3 KiB)
1594738758649.png (23.5 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Alexander Ushakov

OPZV batteries are normally around 85% charge efficiency. So it may be that affecting the sudden jump in SOC

0 Likes 0 ·
Alexander Ushakov avatar image Alexander Ushakov Alexandra ♦ commented ·

I figured out the real cause of such a jump in SOC; according to the batteries manual absorption time should be 2 hours a day at 2.45V and then it should be float mode at 2.35V. So at 11:30 absorbtion was over and float mode started, resulting in significant drop of voltage and charge current and therefore increasing SOC. I changed charging parameters: reduced absroption voltage down to 2.4V, float voltage to 2.3V and increased absorption durationfrom 2 to 12 hours. Let's see.

If OPzV are 85% of charge effeciency, should I input this number into charge effeciency cell in VEConfigure then?

0 Likes 0 ·
1594781504369.png (43.8 KiB)
1594781512459.png (75.7 KiB)
1594781523386.png (44.1 KiB)
Alexandra avatar image Alexandra ♦ Alexander Ushakov commented ·

@Alexander Ushakov

It will help your battery monitor keep better track of your SOC. So yes I would change that.

And thanks for the information on the charge parameters. I am very interested to hear the results of your new configuration from the manual recommendations.

0 Likes 0 ·