EasySolar-II 48/3000/35-32 MPPT 250/70 GX overheating MPPT on full solar load

I have installed the "new" EasySolar-II 48/3000/35-32 MPPT 250/70 GX where everything is in one chassis.

When solar side is running on full power (70A) after 2-3 hours I always get a MPPT Charger Alarm "Overheat Charger Connection" (translated from german "Überhitzung Ladegerätanschluss").

When I reduce the max power to 55A via Victron Connect all is fine. When I move to 60/65/70A I get the error when on full load for 2-3 hours.

Looking into the chassis I can see that a complete MPPT 25/70 was installed in the chassis without any modification. The MPPT easily can go up to 40-50°C on full load.

From my perspective this is a design issue of the full box, because the heat can not be sufficiently transported out of the chassis.

For testing purposes I put an external fan below the MP chassis and then it continuous working without a shutdown - what proves my assumption.

Any similar experience? Is there a way to give the MP back to Victron?

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
yannick avatar image
yannick answered ·

What is the temperature in the room where the unit is installed? If there is a high ambient temperature, this could be the problem.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @mbad

Can you please check if the cables to the MPPT don't overheat? check if all connections are tight.
This shouldn't happen of course, but please check to make sure.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mbad avatar image
mbad answered ·

@Daniël Boekel (Victron Energy Staff) the MPPT is in the Victron integrated:



Cables are tight.

Room temperature on a sunny day between 25-30°C.

I have a 2nd installation with MP 48/5000 and external MPPT 250/85 that has no issues in the same room.

So for me looks like a design issue putting the MPPT into the Easysolar-ii.


1594672961051.png (3.0 MiB)
8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mbad avatar image mbad commented ·

@Daniël Boekel (Victron Energy Staff) are there any other customers with similar experience? Can you check with the Victron team?

If not what would be the process e.g. to replace the MP? It's just 4 months old.

Thanks!

0 Likes 0 ·

Hi @mbad

Yes I've just asked internally, will update if I have answers.

In what orientation is the unit mounted?

0 Likes 0 ·
Show more comments

Hi @mbad

did you remove the front cover to check connections at the MPPT? the error message is about the temperature at the cable connections on the MPPT.

next step would be to contact your dealer to resolve this.

0 Likes 0 ·