RCD Tripping randomly

I have just about installed Multiplus 48/1200/13 and hooked it up to Li-ion 14s1p batteries.

It has been working perfectly in UPS mode and pass through. To test the capacity, I turned off the mains and the UPS kicked in, I let the system run - till the cut off voltage was reached.

When I turned on the grid/mains - the RCD (on the mains consumer unit) tripped. It did this a few times. I disconnected the load and the same happened (rocker switch in ON position). Then I switched it to charger and it did not trip.

I tried various combinations and unfortunately - the RCD tripping is very random and not reproducible.


AC in comes from the grid

AC out goes to feed a total of 250W (a few pumps)

Any input or help would be appreciated.

MultiPlus Quattro Inverter ChargerGeneratorGrounding
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

A system wiring diagram would help with the troubleshooting.

0 Likes 0 ·
8 Answers
ispookie666 avatar image
ispookie666 answered ·

Wiring diagram - Hope this makes sense


If the low voltage does not kick in(when I don't let the batteries run low) - the system functions perfectly; UPS kicks in and auto transfer works perfectly and the Multiplus charges the battery.


But if the Multiplus shuts down due to low voltage and if the mains come on, the RCD on the main consumer unit trips - If there is AC Load connected. Without any AC Load the RCD does not trip. This situation continues till battery voltage is above low battery voltage alarm.

I have a feeling its something very simple I have over looked.



1595435738881.png (11.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwfrary avatar image
jwfrary answered ·

Can you give us a photo of your mains consumer box.

I’m wondering if you have a rcbo and your not tripping on a ground fault but a current.

Also the obvious check your wiring for chafe, or stray strands at the connections etc.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ispookie666 avatar image
ispookie666 answered ·

The RCD which trips is the one on the left.


As I mentioned in the subsequent post - this only happens when Mains power is restored after Multiplus shuts down due to low battery voltage and with mains pass through.

If it was a fault in wiring, I would have thought the RCD would trip regardless.


9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image ejrossouw commented ·

Is the multi case earthed and how? In a fixed installation, you only need use the earth from the ACIN and ACOUT. Also don't discount a faulty RCD.

0 Likes 0 ·
ispookie666 avatar image ispookie666 ejrossouw commented ·

It is a fixed installation and the Multi case is not earthed(I hope you are referring to the earth pin on the case, at the lower end). The ACIN is earthed as normal from mains, and the ACOUT is wired as required including the earth.

0 Likes 0 ·
Show more comments
bruces avatar image
bruces answered ·

Please give details of where this install is located?

Country?

House, boat, motorhome etc?

Installed by licensed electrician? (who knows local regs.. MEN etc)

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ispookie666 avatar image ispookie666 commented ·

Country - United Kingdom

Installation - Home (static)

Installed by myself - the N E L on ACIN and L E N on ACOUT, and the batteries are Yuasa LEV40 14s with a DALY BMS (the tripping occurs even without this BMS).

I have added the Grid code in VE BUS

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ ispookie666 commented ·

You have 2 rcd's, both after the multi output?

0 Likes 0 ·
ispookie666 avatar image ispookie666 klim8skeptic ♦ commented ·

These RCDs are on the consumer unit, the one on the left is the one which trips - which protects the wiring from where the Mulitplus ACIN comes

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ ispookie666 commented ·

The question was "are both rcd's after the multi".

I cant see in the breaker box.................

Where I live, series stacking rcd,s is not good....

0 Likes 0 ·
ispookie666 avatar image ispookie666 klim8skeptic ♦ commented ·

Both RCD's are before the Multiplus. Each RCD controls a different ring. The RCD which is monitoring the ring which supplies the multiplus, trip. I have managed to work around this using two DPDT relay, which suggests it is all to do with Neutral to earth link problem.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ ispookie666 commented ·

I followed the Easysolar wiring, and used a double pole MCB before the Multi, and a RCBO after the multi.

0 Likes 0 ·
easysolar.jpg (57.1 KiB)
ispookie666 avatar image
ispookie666 answered ·

I Added a DPDT relay to provide dual source of power to my critical equipment - I was able to consistently create the RCD tripping. When the Multiplus was in the inverter mode and the backup power(Separate mains power) came on but the Multiplus input AC was off, the RCD kept on tripping. I guess this points to N to E linkage problem.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ispookie666 avatar image ispookie666 commented ·

Managed to circumvent this by adding a second DPDT relay for the Neutrals (victron output and backup power).

After all this, I believe - when the Victron shuts down following low battery, the N to E link is not broken, causing the RCD to trip when the mains come back.

I'd really appreciate if anyone can verify if this is what is expected.

0 Likes 0 ·
tedr avatar image
tedr answered ·

Have you tried to disable the "Ground Relay" setting?

1614466397089.png


1614466397089.png (126.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Carlos Carvalho avatar image
Carlos Carvalho answered ·

Still facing this issue? I am having this exact problem

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tedr avatar image
tedr answered ·

I have solved the problem with better connected Earth Spike. There was a bad earth connection. Now my neutral and earth are at the same level.

2 |3000