I have a single phase system with 2 x Mulitplus II 5000's and 8 x US3000 Pylon Tech batteries.
The Pylon BMS seems to hit a standstill at 88%, glitch???
The system started shutting down sporadically without any fault indication or errors reported.
I looked into it and saw that the systems charges up and when it gets to 88%, the SOC doesn't advance but current is going into the batteries, it then jumps up after a while to 96%, so it seems the SOC is not reporting correctly in this time. This is happening every day, but once in while the whole system will shut down in exactly this time period for a completely unknown reason.
This is the typical scenario when the system shuts down:
There are no errors or notifications I can see of why the system turned off.
Also of concern is that the max charge and discharge currents show under battery parameters are 296A, indicating the data for 4 batteries and not 8. This was like this before I installed the hub and after.
I spoke to a local victron support agent and he said he had the same issues on a site and installing a Pylon Tech LV communication hub sorted out his problem. I installed the hub and everything seems the same. The max charge and discharge currents are still 296A and the system still get's stuck at 88% and the very next day the system shut itself down again without any fault indication.
The hub seems to be working correctly as it's showing a blinking light on the second light, indicating 2 connected banks, all 8 Pylons are all flashing lights in sync.
The DVCC settings are as follows:
The only thing I changed is that SCS - Shared current sense was OFF, I turend it ON to mach the settings that is working fine in my BYD system. I did that today after this last system failure.
I have many sites running with Pylon's and GoodWe hybrid inverters that haven't given me a day's problems, I also a have a 3 phase site with Multiplus II's and 3 x BYD 11.8 B-Box's that is running perfectly.
I really need help understanding how to solve this issue.
Thanks
Andries