we have a customer requesting a solar system for oxygen pumps in his fish farm, he has 4 oxygen pumps each of 2.2 kW rated power and they are three-phase he needs to operate them 24/7 there is also grid in the site for 8-10 hour per day and there is also a generator, he wants to operate using solar during the day time and about 2 hours battery backup at night or during a cloudy winter day, and the Genset will start when the batteries are empty and there is no grid.
can we offer him a solution with Victron at this big back-up capacity, also note that there is no suitable place for the battery so we have to create a small cabin and cool it with a small 12000 BTU AC
I thought of :
19.44 kWp solar (54 panels 360 watts divided for three sets each 18 panels for each inverter)
3 x 5 KVA Quattro
3 X 250/100 MPPT charger (1 for each inverter)
24.576 kWh battery ( 12 X LiFePO4 Battery 12,8V/160Ah Smart ) considering 85%DOD
SO MY QUESTIONS ARE:
1- can this combination (especially the inverter) stand the starting current of this load ( I don't know the starting current the pumps are installed and I couldn't find their datasheet online but I attached the nameplate photo)
2. can I replace the batteries with LONG LIFE GEL OPZV 2V with considering 60% DOD, will they stand the discharge current of the load since the load during the battery back up?
- I attached the load calculation and the motor nameplate
thanks