question

Patrik Kall avatar image
Patrik Kall asked

Smart BatteryProtect BP-100 Remote doesn't work

I recently installed my new Smart BatteryProtect BP-100 for a pure resistive load (Orion-Tr 24/12-20 and a bunch of 12V lamps and a small fan for a toilet, max load about 6A).

I have a ElectroDacus SBMS0 BatteryManager that controls the Remote input via an optocoupler.
When testing the system in a testbench at home everything worked as planned, BP-100 switched off at 2.9V at one of the LiFePo4 cells

Now the BP-100 is installed with a Ground wire to the negative Busbar, The IN to the positive Busbar, via a 100A fuse. The Remote contacts are connected to the SBMS0 optocoupler output.

Testing the function by disconnecting the Remote plug reveals that the load is still On (batteries are fully charged so the output from the SBMS0 is not a viable way of testing).
Testing via the VictronConnect App by deactivating the Load Output yields the correct result, i.e. Load is turned Off, activating Load turns the Load On.

But the removing/replacing the Remote plug doesn't do anything.

Tested the various settings A, B and C in the App, no change whatsoever.

The BP-100 is NOT used to control my Victron 24C1600 Inverter.

When removing the power to the SBMS0 (BMS) the inverter is disconnected (separate optocoupler that opens) but the BP-100 is still on.

// Patrik

Battery Protect
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
nebulight avatar image
nebulight answered ·

I assume you have the output of the orion going to the BP and not the input?

I had a the exact same issue with my BP65. I had no loads connected and just getting it connected to my phone and testing as a backup for an existing BP65 in my camper van. It worked a few times, then I had the exact thing happen. The app was reporting it was still active even when I pulled the remote plug. I tried everything then I posted here and someone from Victron mentioned that I should contact my reseller for a replacement. Once I got my new unit, it was fine. Maybe a bad batch?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Patrik Kall avatar image
Patrik Kall answered ·

Thanks for your respone, nebulight,

I have the Orion on the 24V Output of the BP-100 and from the 12V Output from the Orion I have the Load (only lamps and a small fan).

What I need to check is if the 90sec delay is active and kicks in and thus "fooling" me into believing it is not working...

However, when doing the pre-tests, pulling the Remote disabled the Output immediately, so something has definitely changed.

The cabling to the BP-100 is about 2m (total) away from the battery, but every cable, busbar and connection is overdimensioned, so I have only 0.1V voltagedrop.

The picture shows the design before actual testin/installation in my cottage.

50sqmm cables from the battery to busbars, 16sqmm from busbar to fuse and then to the BP-100.


img-4978.jpg (2.3 MiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nebulight avatar image nebulight commented ·

In your application, you should use Li-Ion mode and there is no 90 second delay.

I'm worried if you some how damaged the mosfet inside with the DC-DC converter. While it's not an inverter, DC-DC converts still have an inrush current that could be too high for the BP.

However if the only thing going through the BP is the Orion, you can just use the Optocoupler on the SBMS to control the remote port on the orion instead of going through the BP. You can get rid of the BP all together.

0 Likes 0 ·
Patrik Kall avatar image Patrik Kall nebulight commented ·

The Orion is a version without remote control input, hence the reason for the BP-100.

Well, the BP-100 might be faulty, however I cannot fathom that the inrush current could be 40-45 times the actual load of the output of the Orion.

My lamps draw approx. 2A and the fan 0.3A.

The BP-100 is hugely overdimensioned for my needs ( I used to have a 24V refrigerator which died before I got to install the BP-100, and is now replaced with a 230V version on the inverter (which is not controlled by the BP-100))

AND, it works from the Victron Connect App, without any delay... On/Off/On/Off indefinately.

I think I need to contact seller.

Many thanks for your input nebulight, it's highly appreciated!

0 Likes 0 ·
boris avatar image
boris answered ·

What is a set up on BP-100??


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.