I have installed 3 x Pylontech US3000 an a Venus GX device. CAN Bus BMS is sset according to https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom but I don't see y pylontech entry on venus. I checked the wiring of the can cable as in https://www.victronenergy.com/live/battery_compatibility:can-bus_bms-cable all OK, terminator set. What can be the reason that the battery is not shown on venus?

Do I have to set anything else? Are there any settings on multiplus needed that the battery is shown?

Pylontech
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Can you please post a few photos of the installation?

Are you using the VE.Can port with the plug, or the can port with the terminal connectors on the Venus GX?

Are you using the official Victron Type B cable or a self made cable?


0 Likes 0 ·
nemo5 avatar image nemo5 Guy Stewart (Victron Community Manager) ♦♦ commented ·

i replied to myself, so see below...

0 Likes 0 ·
2 Answers
nemo5 avatar image
nemo5 answered ·

Thanks for your answer.

I use the official Type B cable with VE.Can port. CAN-Bus (1) set to CAN-BMS (500k)



2.jpg (52.6 KiB)
3.jpg (43.1 KiB)
4.png (12.6 KiB)
8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Just to rule it out, can you please take a screenshot of the services menu options on the GX device?

0 Likes 0 ·
nemo5 avatar image nemo5 Guy Stewart (Victron Community Manager) ♦♦ commented ·

I have switched to english now.

0 Likes 0 ·
5.png (17.9 KiB)
Show more comments
nemo5 avatar image
nemo5 answered ·

Today I had done some meassurments on the CAN-Bus with my multimeter (DC-Values):

1) Typ B CAN Cable on Pylontech, meassured on Victron Side of Cable without venus and without termiantor: GND to CAN-L: 1,7V, GND to CAN-H: 3,1V -> OK

2) CAN Cable connected on pylontech and venus, meassured on venus without terminator: GND to CAN-L: 0V (~3mV), GND to CAN-H: 0V -> Venus seems to shorten CAN Signals!

3) CAN Typ B Cable only on venus, no terminator: GND to CAN-L: 0V, GND to CAN-H: 0V -> CAN bus on Venus is not working


I had also meassured that one CAN-Bus Terminator has about 30Ohm instead of 120Ohm. Maybe this wrong victron terminator had killed venus can bus?


On Venus ifconfig gives me:

can0      Link encap:UNSPEC  HWaddr 
00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00  
          UP RUNNING NOARP  MTU:16  Metric:1
          RX packets:67 errors:0 dropped:0 overruns:0 frame:0
          TX packets:0 errors:0 dropped:20 overruns:0 carrier:20
          collisions:0 txqueuelen:100 
          RX bytes:536 (536.0 B)  TX bytes:0 (0.0 B)
          Interrupt:167 


without can cable attached. RX does not increade when pylontech is connected, but understandable because venus seem to shorten can signals.