MultiPlus 2 no connection to the grid possible

Hello all!

I have a multiplus 2 (48/3000)
All works fine, but when I put it on the grid
then he goes out.

- Bulk is blinking
- Float lights up
- Inverter ON is blinking

If I disconnect the grid after a few seconds, the inverter is on again and supplies the consumers from the battery / PV

A Mk3 to USB and the VEconfig tool is available to make any changes.

By the way:
- ESS switched on or off makes no difference.
- Charger mode is off.
- Virtual switch is off.

If further information is required to solve the problem, please let me know!


Thanks!

Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

florian-s avatar image florian-s commented ·

Many thanks!!


Neutral and Phase was invertet. From distribution box to the garage.