question

Andreas Jaunsen avatar image
Andreas Jaunsen asked

BMS and HE Li-ion capacity messed up after updates

Hi recently returned to the boat which had been on shore for past 10 months (not connected to power). 2x Li-ion HE Batteries (2x200Ah) seemed okey so started updating all systems (Venus GX, multiplus, mppt, BMS400 etc).


I notice in the past week that the battery level seems to be wrong. I reset consumption stats but still at about SOC 60-65%, voltage will be <24.5v indicating it is much closer to empty.

At this 65% SOC level the multiplus also turns off by itself and no longer inverts... again suggesting SOC is wrong!

I am not getting multiple low cell voltages and have no idea how to solve this?!!

MultiPlus Quattro Inverter ChargerBMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi, best (and only for most battery monitors, probably also the HE batts + Lynx) way to sync the calculated SOC with the actual physical state of charge is to fully charge the battery.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark commented ·

Sorry to jump on to this ....but the synchronisation button on the Lynx Ve-Can shunt doesn’t work!

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ Mark commented ·

Hi Mark, ok I’ll look into that.

0 Likes 0 ·