question

tahoematt avatar image
tahoematt asked

Fuse size for MPPT 100/50

I’m installing a mppt 100/50 in a van build. I have 3 -180 watt panels wired in a series. I have a 15amp dipole disconnect between mppt and the panels but what size fuse should I use between the busbar and the mppt? I was guessing 75amps or 100??

MPPT Controllersfuses
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Vance Mitchell avatar image
Vance Mitchell answered ·

It depends on the cabling that you are using between the busbar and the MPPT.

Generally I would use around 150% of expected max current (75A in this case) as a guide but only if cabling is sized to suit.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tahoematt avatar image tahoematt commented ·

I plan to use 4AWG - will that fit? So 75amp fuse?

0 Likes 0 ·
Show more comments