question

Justin avatar image
Justin asked

Multi Plus Compact - in Passthru mode ?

hi there,

we have a MultiPlus Compact 12/1200/50-16 that seems to be stuck in passthru mode once it completes the bulk charge and never gets to Float and storage this site is slightly different where is has a Energy Meter ET112 to keep track of the AC input power used as we need to power for the grid power used

thoughts on how this can be fixed ?

thanks

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

If you disable the Grid Meter does it leave passthru mode after 10 minutes or a restart?

The causes of Passthru are usually addressed by one of the issues in Question 4 of the ESS FAQ.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin avatar image Justin commented ·

hi Guy,

thanks for your reply can to tell me how to disable the Grid meter ? can this be done from the CGX ?
0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ Justin commented ·

Hi @Justin

you can do this in the ESS-menu (yes in GX device, either on screen or with remote-console)

0 Likes 0 ·
Justin avatar image Justin Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

thank you i'll log in via the remote console from the VRM and have a look

0 Likes 0 ·
Justin avatar image Justin Justin commented ·

does this look right ?

0 Likes 0 ·
1592565694684.png (10.5 KiB)
Show more comments