question

meshugga avatar image
meshugga asked

BatteryProtect - 220AMP - reset time

The nominal power draw on my 24v bow thruster is 500 A. Generally only used for about 30 seconds at a time, which is within the 600A intermittent range. However, if the BatteryProtect does trip, seems that it takes 90 seconds to reconnect. In a tight mooring situation with side winds, this is obviously completely unacceptable, and thus I should not install this unit.

Is my conclusion correct or have I misunderstood something here?

Battery Protect
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Meshugga

Where did you read it can withstand 600A for that long?

I did find that it should reconnect after 30 seconds:
"Load reconnect delay 30 seconds" but maybe it has to cool down first after the overload?

I wouldn't use a 220A device for such high current that has to be sustained if needed. I'd connect the battery directly and use a Battery Protect output to the control relay so it disconnects the relay signal instead of the high current path.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

meshugga avatar image meshugga commented ·

HI Daniel. Thanks for the response.

Got my info from the datasheet:

* Peak current (during 30 seconds) 600A

* Load disconnect delay 90 seconds (immediate if triggered by the VE.Bus BMS)

* Load reconnect delay 30 seconds

A question on your recommendation: How would the BP activate if it is only connected to the small control relay current? Seems to me it is essentially just a circuit breaker.