question

bbrouwer avatar image
bbrouwer asked

For DC wiring of a Victron Multi 1200/50 di I need cable glands or can I direct connect the cable inside the scrwe terminal. Thanks

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
solarhack avatar image
solarhack answered ·

I assume by Glands, you mean Ferrules. It is generally advised to use Ferrules on connection points when you are connecting multi-strand wires . This essentially makes a multi-strand wire behave like a solid wire at the connection point. The connection is usually more mechanically sound. Splayed wires are less likely to pop out of the terminal and the connection resistance is lower and stays lower over time (Not as good as solid but significantly better than a raw multi-strand).

Here is an interesting link https://www.ee.co.za/article/ferrules-insurance-connection-failure.html

and you should also look at Victron's unlimited wiring guide for general advice on wiring https://www.victronenergy.com/upload/documents/Wiring-Unlimited.pdf

Hope that helps

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.