I'm planning to acquire a 60v battery pack. Can the MultiPlus II work with this voltage? I will have a separate charge controller for charging the battery, so the requirement is only the inverter application, not charging.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I'm planning to acquire a 60v battery pack. Can the MultiPlus II work with this voltage? I will have a separate charge controller for charging the battery, so the requirement is only the inverter application, not charging.
You did not say whether that 60V is the fully charged Voltage or the nominal Voltage.
I assume it is the nominal Voltage, in that case, make sure the battery Voltage never exceeds 66V.
I don't think these parameters would be suitable for a nominal 60V battery, I wouldn't recommend using a 60V battery with a 48V appliance.
The Voltage range for a 48V MultiPlus is 38V to 66V. Do not exceed 66V!
Datasheet: https://www.victronenergy.com/upload/documents/Datasheet-MultiPlus-II-inverter-charger-EN.pdf
You said you are not interested in charging, but because the MultiPlus is also a charger anyway, the maximum Absorb Voltage is 64V for your information.