Firmware rollback on Multi + 48/5000/70-50

I am in need of the 1959143.VFD file to roll back firmware on Multi + 48/5000/70-50

firmware update
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Frans

both 1959159.vff and 1959209.vff are available on Victron Professional

why do you need 143?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frans avatar image
frans answered ·

Maybe the file extension .VFF ?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frans avatar image
frans answered ·

After upgrading to 195159 with batteries fully charged I get intermittent trip and restart even with relatively low load added. Indication on inverter "low bat + temperature" LED. The system worked perfectly with the 143 firmware. Also at times change over to shore power with high loads but also not as programmed.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.