2020_05_25 Inverter power limit not working.pdfHi,
I set limit inveter power in ESS, but It doesnt seem to work. My limit was 700W but it was still inverting around 2000W and only 300W was drawn from the grid. Do you know where could be the problem?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
2020_05_25 Inverter power limit not working.pdfHi,
I set limit inveter power in ESS, but It doesnt seem to work. My limit was 700W but it was still inverting around 2000W and only 300W was drawn from the grid. Do you know where could be the problem?
Hi @jiri rysavy
What is your AC input current limit set to? (devices, multi, input current limit), That AC input current limit will override the ESS setting and restrict the power supplied from the AC input (as a higher priority).
I see green+orange 'led' on in the screenshot...
Thanks, my AC input current limit was set to 1. Now, the parameter 'Maximum inverter power' works fine.
But the green and orange diodes for "mains on" and "bulk'' are still on, plus "Invertor on" is flashes. Is that wrong?
No nothing wrong, it means it's delivering power from battery to loads (or grid)
ESS design and installation manual