Setup (in an RV):
* 2x MultiPlus 24/3000/70-50 120V set up in master-slave configuration
** One each connected to a circuit breaker panel
* SmartSolar MPPT 150/70
* Color Control GX
* BMV-712
AC panels have loads distributed across them. Included among these are two RV aircon units, with soft-start capacitors added. When I run a specific RV aircon unit, which is on one panel, and another high-wattage device on the other panel, I get VE.Bus Error 5 and the accompanying 30-second shutdown of all AC loads.
Testing so far:
* Seems to be centered around the interaction between the inverters, one of the aircon units, and the solar system.
* Only happens when inverting. When on shore power, no issues.
* Seems to only happen when the compressor on the AC comes on.
* Second AC unit does not appear to generate the problem.
* Load at the time is anywhere from 1600 - 3000 W, depending on what I have running. Seems to initially require me to put a heavy load on the system, then I can get it to happen with solely the AC unit in operation.
* Slave unit always displays the fault. This inverter drives the aircon unit that I can generate the fault with.
* Have not tried cutting out the PV controller completely...so far have only cut the panels out (400A panel cutout switch, 80A controller cutout switch)
Any ideas appreciated.