End of absorption with tail current

Hello. I wonder if I am thinking this right... I am trying to end the absorption phase solely based on the tail current, but it seems system is ignoring that.


Scenario is: Charging LiFEPO4 bank with 8 cells (25.6V) with integrated BMS just for protection (no communication with Victron)

- Multiplus 24/ 3000

- 3x MPPT in parallel charging

- Venus GX


Customised charge profile:

- Absorption voltage: 27.6 V (I can monitor cells, and no cell is above 3.6V)

- Absorption time: Fixed, 1hour 30 minutes

- Tail current: 9 amps, battery capacity is ~180Ah

- Float voltage: 27.1 V


It ignored the tail current and the absorption time was exactly 1,5 hours. I would like to stop absorption when current decreases past 9A.

I didn't feel adaptive time was ok for lifepo4, as if bulk takes longer, absorption may not need so much time. I would like to make the criteria to stop Abs be solely the Tail Current (system!, not individually each MPPT)

How can I do this?

battery chargingLithium Batterymppt charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mark avatar image
Mark answered ·

I have been using tail current to end absorption phase for some time now and it's been working very well.

I initially used the solar charger output current and then switched the DVCC - SCS when the feature was released with the BMV battery monitor as the tail current source.

However I have a single large MPPT, so it might be a compatibility issue when using the tail current feature with multiple MPPTs in parallel - linked by VE.Smart Network.

I will try to find out for you.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Elimac avatar image Elimac commented ·

Mark, is the presence of the BMV a mandatory condition? As System current is already known in my case, even without BMV, I was hopeful it wasn't needed. But, in SCS I can't detect any monitor...

0 Likes 0 ·
Mark avatar image Mark ♦♦ Elimac commented ·

I just got feedback that the tail current feature should work fine with multiple synchronised MPPTs and no battery monitor.

To trigger the end of absorption, the sum of the MPPT output/charge current from all MPPTs must fall below the tail current threshold set for 60s (while the charge voltage setpoint is also maintained).

Can you confirm that all of these conditions were met during your testing?

Note that without a battery monitor in the system and DVCC - SCS active, it will not use the actual current flowing into the battery, only the MPPT output current, so if you are also powering loads at the same time they will not be considered. (The battery current 'calculated' by the GX device from the Multi & MPPT cannot be selected as a source for SCS)

0 Likes 0 ·
Elimac avatar image Elimac Mark ♦♦ commented ·

A-AH moment... if it considers the MPPT current and not battery current, then one must consider all the System load too!! That can explain it!!!

1 Like 1 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ Elimac commented ·

I confirm: even though your GX Device knows battery current (by calculating it from mppt-reported current and Multi-reported current), your mppt does not know the battery current.


it only knows its output current (or in your case total Output current of all synced mppts together) and thats what its using to evaluate the tail current threshold with.

1 Like 1 ·
john-hagtharp avatar image
john-hagtharp answered ·

Are you running ESS & DVCC? If my understanding is correct, this would place the MPPTs under external contol using the charge algorithm from the Multiplus.

Unless I missed something in the changelogs, I don't believe you can set a tail current in the Multiplus. Adding the new charge algorithm capabilities from the MPPTs into the Multiplus is something I've been meaning to request some time.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Elimac avatar image Elimac commented ·

Only DVCC (mainly due to the charge current limit necessity). No ESS, it is a (nearly) offgrid system.