question

tinybluehouse avatar image
tinybluehouse asked

Battery and 712 show different voltages

While my 200ah 12v smart lithium battery was in absorb I happened to check in on the app and the battery over Bluetooth was showing 13.21v while the bmv was showing 14.21v which is slightly worrying. The shunt is connected to the battery via 70mm2 cable to the 2000kva inverter as per the manual.

BMV Battery MonitorLithium Battery
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tinybluehouse avatar image tinybluehouse commented ·

When I turn the PV off, battery drops to the same voltage on bmv as battery over Bluetooth.

0 Likes 0 ·
1 Answer
nigelfxs avatar image
nigelfxs answered ·

Hi @Tinybluehouse

Have you checked the in-line fuse to the BMV-712? It should be a 1A type - not 100mA. There have been some reports of bad readings when fitted with a 100mA fuse.


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tinybluehouse avatar image tinybluehouse commented ·

It’s 100ma fuse down it’s not that

0 Likes 0 ·
tinybluehouse avatar image tinybluehouse commented ·

I totally read that wrong!!! So I need a 1A fuse not the 100ma I have installed. Are they just standard fuses? They look smaller

0 Likes 0 ·