Multiplus Ignore AC in split phase

I have (2) Multiplus compact 2000 units in split-phase configuration and "switched as group" is unchecked. I can only get the Mulitplus on line 1 to work with "ignore AC" and successfully switch over to AC when the load is above the set limit. The other Multiplus will always ignore the AC and never connect even when the load is beyond the set limit. Both inverters have the exact same settings. What am I doing wrong?

split phase
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @djpollock

can you share the assistant summery of both inverters?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

djpollock avatar image
djpollock answered ·

I did not use the assistant. I used the "dedicated ignore AC" option with the virtual switch. It is set to connect to AC at 1600w, disconnect at 1400w, and connect at 12v, disconnect at 13.2v.