Can a Skylla TG 48/50 charger synchronize with VE.CAN charge controllers?

Hello,

Can a Skylla TG 48/50 charger synchronize with VE.CAN charge controllers to provide a controlled charge to a common battery bank where several VE.CAN charge controllers are already charging?

I thank you in advance for your assistance.

Kind regards,

chargerVE.CanSkylla
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Sorry but no, these units will not synchronise charge states.

They will all work fairly nicely on the same DC bus via monitoring battery voltage though. Are you worried about a particular affect by not having them synchronised?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tango avatar image tango commented ·

@Guy Stewart (Victron Community Manager)

Hello,
For my below mentioned "goal" of using the Generator as Backup should I run into an time of "not enough sun" as described here:

https://community.victronenergy.com/questions/237143/buffering-the-battery-with-a-generator-3-phase-sys.html?childToView=237365#answer-237365

I would just like to see if there is a good way to set it up / control it.
Sadly there is no update on a 48V Skylla i so it seems to me a Manual setting via Dip switches to the Charge Current I want is the only way with a Skylla TG 48V/80 unit.

Otherwise a Single Phase Generator (on only one MP L1) will not work for charging. (Or am I mistaken?)

0 Likes 0 ·