Have just installed a 712 battery monitor to 12v battery bank. Voltage seems to be showing a little high?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Have just installed a 712 battery monitor to 12v battery bank. Voltage seems to be showing a little high?
Thank you, yes grid was connected. As soon as I disconnected voltage dropped to 12v.
Hi yes you are correct I was still connected to the grid as soon as I disconnected from grid the voltage dropped to 12v
In that case I think the shunt isn't wired correctly.
When a charger is running you should have see a positive current/power running into the battery. But in you screenshot above there are 0A and 0W.