2 MultiPlus in parallel, turning off

I have two MultiPlus 12/3000/120 in parallel connected to a CCGX controller. After using either the controller or the power button on the front of the unit to turn off the Multiplus to turn them back on you must first use the controller or power button, but then you must unplug and replace the communication cables, in the correct sequence. Until you do that the units remain dark and unresponsive. You must first unplug the slave and once the lights start flashing you plug the cable back into place, then unplug the master, wait for flashing lights and then plug in the cable again. The units them work well until the next time that the power state is changed.

Of course the problem with this is that I must leave the cover off of the Master so that the cables are accessible and reaching into the unit is potentially a shock hazard.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Turning off and on again with the CCGX should work without unplugging cables.

But if you use the switch at the unit itself this can happen.

Because of that a multi-phase/parallel system always have to be switched off/on with a remote switch (DMC, VE.Bus smart dongle or GX device).

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

karl-leibensperger avatar image karl-leibensperger commented ·

I have just verified that turning off and then on again via the CCGX does NOT reconnect the devices until the cables are unplugged and reconnected.