I would like to have more control over the equalization period and how often I can start it.
My 24 V lead-acid cells are sulphated. My battery manufacturer suggests an equalization period of 5 hours at 31.5-32.0 volts. Our Multiplus allows only a 1 hour eq period when started from CCGX. If I try to start another eq period immediately after an eq period has finished, the CCGX tells me that eq is "Starting ..." but does not actually start an eq cycle ie bulk and absorption LEDs are not flashing; battery volts oscillates between about 31.5 and 28 V.
Is there built in to the Multiplus software a limit as to how often you can perform an eq? And for how long? Is it possible to change these?
Is it possible to do this another way, by setting the absorption volts to 31.5 (my desired eq volts) and starting an ordinary charge?