Hi,
i'm running a Multi 12/500 in my Van, combined with 150Ah LiFePo4 Batteries, MPPT and 200Wp PV.
Is it possible to feed unsused Energy back to the Grid if it's not used for Charging the Batterie?
Do i use ESS for that?
Thanks in Advance.
Hi,
Yes you could use ESS, select the feed excess option .
Regards
If its installed in a van, this means you have some form of mains connector that you can unplug to drive?
If this is the case, you should not set up ESS as the plug connector can remain live for some time after disconnection.
ESS design and installation manual