Hi,
i'm running a Multi 12/500 in my Van, combined with 150Ah LiFePo4 Batteries, MPPT and 200Wp PV.
Is it possible to feed unsused Energy back to the Grid if it's not used for Charging the Batterie?
Do i use ESS for that?
Thanks in Advance.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
i'm running a Multi 12/500 in my Van, combined with 150Ah LiFePo4 Batteries, MPPT and 200Wp PV.
Is it possible to feed unsused Energy back to the Grid if it's not used for Charging the Batterie?
Do i use ESS for that?
Thanks in Advance.
If its installed in a van, this means you have some form of mains connector that you can unplug to drive?
If this is the case, you should not set up ESS as the plug connector can remain live for some time after disconnection.
ESS design and installation manual
Additional resources still need to be added for this topic
16 People are following this question.