VRM alarms contradicting each other?

For some reason, all the VRM alarms always arrive in pairs. One that flags the warning, and one that apparently immediately cancels it.

Example:

Problem: low battery

Recovery: low battery


However, I know that the problem is NOT recovered, since I have to manually plug in shore power to rectify it.

So why the constantly double (and contradicting) emails?





VRM
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @johannes.hovda

This is probably because a load (the inverter?) shutdown due to low battery alarm, and the battery voltage came back up a bit to clear the alarm and go back to warning state.

Depending on what component sent the alarm ('bussen'?), changing settings in that device can change this behavior.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johanneshovda avatar image johanneshovda commented ·

I have a multiplus and a bmw-702.
Both are connected to a Venus GX in a converted touring bus ("bussen").
So perhaps they are both fighting?

have chosen the Bmw702 as the battery monitor in the VenusGx settings.


How should I configure the alarms to avoid this constant duplication?

0 Likes 0 ·