Modbus/TCP error finding service

Hi,

I have some troubles to with the PLC connected to the CCGX. Can anyone help?

MultiPlus Quattro Inverter ChargerCCGX Color ControlModbus TCP
11.jpg (723.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
frodes avatar image
frodes answered ·

Maybe @mvader (Victron Energy) knows the answer on this one?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Hi, I don't know what is wanted to be queried here. And the query seems to query 434 addresses at once?

I'd start with single register queries, and make sure to super closely read the explanation about register numbers and unit ids in the Modbus TCP documentation:

https://www.victronenergy.com/live/ccgx:modbustcp_faq

Hope that helps!

1 Like 1 ·
frodes avatar image frodes mvader (Victron Energy) ♦♦ commented ·

Thank you @mvader (Victron Energy).

We are trying to write to «Active input current limit» at address 22.

With a scalefactor = 10, the typed qty 434 will be the same as about 43 Ampere per phase. This value will be changed depending in which generator that are online. Function code 6 = «Write singel register» in modbus. We will look closer at the register numbers and unit-IDs, as you have suggested.